I have a 12-2 w ground wire running from my breaker panel to a junction box in my garage. Can I split the b & w at the breaker box to switch it to 2- 110v lines if I rewire after the junction box. I want a second 11ov line in the garage.

_________________
Beautiful and unusual tone woods at a reasonable price.
http://www.rctonewoods.com/RCT_Store
The Zootman
1109 Military Rd.
Kenmore, NY 14217
(716) 874-1498


Top
 Profile  
 
 Post subject:
PostPosted: Fri Jul 14, 2006 9:57 am 
Offline
Contributing Member
Contributing Member

Joined: Mon Dec 27, 2004 11:25 pm
Posts: 7207
Location: United States
I believe when running 110 you need a black, neutral (white) and the ground. So splitting a 220 line isn't such a great idea. You'll have to run another wire. Replace the 220 breaker with two seperate breakers. Hopefully Bruce will drop in, (our official OLF electrician) and set us straight on that, but I'm pretty sure that's the deal if you want two circuits.

_________________
"I want to know what kind of pickups Vince Gill uses in his Tele, because if I had those, as good of a player as I am, I'm sure I could make it sound like that.
Only badly."


Top
 Profile  
 
 Post subject:
PostPosted: Fri Jul 14, 2006 10:13 am 
Offline
Brazilian Rosewood
Brazilian Rosewood
User avatar

Joined: Mon Dec 27, 2004 9:42 pm
Posts: 4217
Location: Buffalo, NY
First name: Robert
Last Name: Cefalu
City: Buffalo
State: NY
Zip/Postal Code: 14217
Country: US
Don I meant turning a 110 line into 2 110 lines by connecting the black to a breaker and the white to another breaker then at the junction box rewiring the garage using the black for one 110 and the white for the other and the ground would be common to both.

_________________
Beautiful and unusual tone woods at a reasonable price.
http://www.rctonewoods.com/RCT_Store
The Zootman
1109 Military Rd.
Kenmore, NY 14217
(716) 874-1498


Top
 Profile  
 
 Post subject:
PostPosted: Fri Jul 14, 2006 10:52 am 
Offline
Contributing Member
Contributing Member

Joined: Mon Dec 27, 2004 11:25 pm
Posts: 7207
Location: United States
I'm pretty sure you still need a black & white & ground for each 110 line to complete the circuit.
Where's Bruce?!Don Williams38912.8290046296

_________________
"I want to know what kind of pickups Vince Gill uses in his Tele, because if I had those, as good of a player as I am, I'm sure I could make it sound like that.
Only badly."


Top
 Profile  
 
 Post subject:
PostPosted: Fri Jul 14, 2006 12:57 pm 
Offline
Cocobolo
Cocobolo

Joined: Mon Apr 24, 2006 4:35 pm
Posts: 298
Location: United States
[QUOTE=Don Williams] I'm pretty sure you still need a black & white & ground for each 110 line to complete the circuit.
Where's Bruce?![/QUOTE]
Don you are right on that. each 110 circuit need a black white and a ground. The method he is talking about would be dangerous and not allowed by any fire code.   


Top
 Profile  
 
 Post subject:
PostPosted: Fri Jul 14, 2006 1:01 pm 
Offline
Cocobolo
Cocobolo

Joined: Mon Apr 24, 2006 4:35 pm
Posts: 298
Location: United States
Bob if you have room for another circuit breaker in the box the safest thing would to be run another new circuit. If you dont you can buy a twin pole space saver breaker at home depot. This splits one loacation in the breaker box to two. This allowed and safe in most areas.



Top
 Profile  
 
 Post subject:
PostPosted: Fri Jul 14, 2006 1:07 pm 
Offline
Brazilian Rosewood
Brazilian Rosewood
User avatar

Joined: Mon Dec 27, 2004 9:42 pm
Posts: 4217
Location: Buffalo, NY
First name: Robert
Last Name: Cefalu
City: Buffalo
State: NY
Zip/Postal Code: 14217
Country: US
Thanks Michael. I wasn't sure if this would meet code or not. The only reason I asked is because getting from the house to the garage would involve a lot of work.

_________________
Beautiful and unusual tone woods at a reasonable price.
http://www.rctonewoods.com/RCT_Store
The Zootman
1109 Military Rd.
Kenmore, NY 14217
(716) 874-1498


Top
 Profile  
 
 Post subject:
PostPosted: Fri Jul 14, 2006 1:20 pm 
Offline
Cocobolo
Cocobolo
User avatar

Joined: Tue Mar 14, 2006 12:41 pm
Posts: 318
Location: Trois-Rivieres
First name: Alain
Last Name: Lambert
City: Trois-Rivieres
State: Quebec
Country: Canada
Focus: Build
Status: Amateur
The safe way would be to run the 220V in the garage in a small breaker panel and then install 110 V breakers in that panel and run lines from there with both black and white.
But I am not an electrician!


Top
 Profile  
 
 Post subject:
PostPosted: Fri Jul 14, 2006 1:26 pm 
Offline
Cocobolo
Cocobolo

Joined: Mon Apr 24, 2006 4:35 pm
Posts: 298
Location: United States
[QUOTE=Alain Lambert] The safe way would be to run the 220V in the garage in a small breaker panel and then install 110 V breakers in that panel and run lines from there with both black and white.
But I am not an electrician![/QUOTE]
That's the misunderstanding. he is not talking about spliting a 220 line he was talking of spliting a single 110 line into two 110's by using the white as one hot and the black as another and use the single ground as a comman for both to gain two seperate 110 lines.


Top
 Profile  
 
 Post subject:
PostPosted: Fri Jul 14, 2006 1:32 pm 
Offline
Cocobolo
Cocobolo

Joined: Mon Apr 24, 2006 4:35 pm
Posts: 298
Location: United States
Bob what is the 110 line you have used for and what do you plan on using on the second 110. There is a way to add a second outlet to from the junction box. But the main amperage for the two outlets would be a 15 or 20 amps combine depending on the breakers max if you use both outlets at the same time. If you exceed that it will trip.Michael Shaw38912.9405787037


Top
 Profile  
 
 Post subject:
PostPosted: Fri Jul 14, 2006 6:49 pm 
Offline
Brazilian Rosewood
Brazilian Rosewood
User avatar

Joined: Mon Dec 27, 2004 9:42 pm
Posts: 4217
Location: Buffalo, NY
First name: Robert
Last Name: Cefalu
City: Buffalo
State: NY
Zip/Postal Code: 14217
Country: US
Michael I put a 10 x 14 storage shed behind my garage and I wanted to run power from the garage to the shed. I'll have a dehumidifier and a fan running and a couple of lights.The only thing I use in the garage is lights and occasionaly my chop saw. I thought I would use the second 110 line for the shed.

_________________
Beautiful and unusual tone woods at a reasonable price.
http://www.rctonewoods.com/RCT_Store
The Zootman
1109 Military Rd.
Kenmore, NY 14217
(716) 874-1498


Top
 Profile  
 
 Post subject:
PostPosted: Fri Jul 14, 2006 8:52 pm 
Offline
Cocobolo
Cocobolo

Joined: Mon Apr 24, 2006 4:35 pm
Posts: 298
Location: United States
You could branch of the junction box with a line but I think the thing that would be a over load would be when you use the chop saw at the same time the fan and dehumidifier are running. The chop saw will draw some amp when you use it. If it was just for the lights the fan and humidifier I dont think it would be a problem.


Top
 Profile  
 
 Post subject:
PostPosted: Fri Jul 14, 2006 10:15 pm 
Offline
Contributing Member
Contributing Member

Joined: Mon Dec 27, 2004 11:25 pm
Posts: 7207
Location: United States
Bob, if you're planning on running between buildings, you will want to use exterior rated electrical conduit, preferably pvc, underground if the distance is much at all. If they are right next to each other, still use conduit, and seal good so the conduit has a watertight entrance to both stuctures.
You can branch off the other simply by using a junction box as Michael said. You'll need to have some slack wire in the grage, or you'll need to replace some. Get a metal J-box for inside the garage with some strain reliefs, and a roll of 12-2. Then get all the conduit you will need to start from inside the garage and go out to the shed. You will need connectors and sealant, or solvent, whatever the guy at Home Depot / Lowes etc recommends to run the pvc outside.
How far is the shed from the garage?

_________________
"I want to know what kind of pickups Vince Gill uses in his Tele, because if I had those, as good of a player as I am, I'm sure I could make it sound like that.
Only badly."


Top
 Profile  
 
 Post subject:
PostPosted: Fri Jul 14, 2006 10:40 pm 
Offline
Brazilian Rosewood
Brazilian Rosewood
User avatar

Joined: Mon Dec 27, 2004 9:42 pm
Posts: 4217
Location: Buffalo, NY
First name: Robert
Last Name: Cefalu
City: Buffalo
State: NY
Zip/Postal Code: 14217
Country: US
[QUOTE=Michael Shaw] You could branch of the junction box with a line but I think the thing that would be a over load would be when you use the chop saw at the same time the fan and dehumidifier are running. The chop saw will draw some amp when you use it. If it was just for the lights the fan and humidifier I dont think it would be a problem.[/QUOTE]
Michael that's what I thought. I think I'll have to bite the bullet and run a new line to the shed.
Don the shed is behind the garage. Distance between them is 2 feet. I plan on using PVC.

_________________
Beautiful and unusual tone woods at a reasonable price.
http://www.rctonewoods.com/RCT_Store
The Zootman
1109 Military Rd.
Kenmore, NY 14217
(716) 874-1498


Top
 Profile  
 
 Post subject:
PostPosted: Sat Jul 15, 2006 1:48 am 
Offline
Cocobolo
Cocobolo
User avatar

Joined: Sat May 13, 2006 4:05 am
Posts: 337
Location: Reno, Nevada
First name: Michael
Last Name: Hammond
Focus: Build
Status: Amateur
Bob:
Hi, I am an electrical contractor by trade. Splitting the garage circuit as you describe will work o.k. However it is generally considered to be very poor practice. You will need to be absolutely certain you get both phases on the 12-2 to the garage, otherwise you will put a double load on the ground wire which is unsafe! What happens is that over a period of time the average person tends to stretch a "stretched" circuit just one more time and you end up with a big mess. If you go ahead and run a new seperate line to the shed you will be able to sleep much better and have room for expansion at a later time. If you have any more questions I will be happy to offer assistance on any technical matters. Good luck...

_________________
The Biggest Little City, Nevada
www.hammondguitars.com
I love building guitars!


Top
 Profile  
 
 Post subject:
PostPosted: Sat Jul 15, 2006 2:01 am 
Offline
Koa
Koa

Joined: Sat Feb 12, 2005 6:20 am
Posts: 1437
First name: Bob
Last Name: Johnson
City: Denver
State: CO.
Zip/Postal Code: 80224
Country: USA
Focus: Build
Status: Amateur
Bob,
Don't stand in water


Top
 Profile  
 
 Post subject:
PostPosted: Sat Jul 15, 2006 3:17 am 
Offline
Brazilian Rosewood
Brazilian Rosewood

Joined: Wed Dec 29, 2004 5:10 am
Posts: 2020
Location: Argentina
Hi Bob, Looks like you got some good advice.

There is a way to use a 12/3 with a ground to make two 110 Circuits with two separate breakers. This is allowed based on the fact that neutral wires don't carry the load that the hot wires do. So a common neutral can suffice two circuits if all wire sizes are the same.

Regardless, I agree with the above comments that safe NEC practices dictate a separate line for your shed. The NFPA is bent on saving our life and property. We don't want no charred zoot.


Top
 Profile  
 
 Post subject:
PostPosted: Sat Jul 15, 2006 5:37 pm 
Offline
Brazilian Rosewood
Brazilian Rosewood
User avatar

Joined: Mon Dec 27, 2004 9:42 pm
Posts: 4217
Location: Buffalo, NY
First name: Robert
Last Name: Cefalu
City: Buffalo
State: NY
Zip/Postal Code: 14217
Country: US
Hey guys thanks for all the great advice. I decided to take the time and run a new line. Better safe than sorry.

_________________
Beautiful and unusual tone woods at a reasonable price.
http://www.rctonewoods.com/RCT_Store
The Zootman
1109 Military Rd.
Kenmore, NY 14217
(716) 874-1498


Top
 Profile  
 
 Post subject:
PostPosted: Sat Jul 15, 2006 5:39 pm 
Offline
Cocobolo
Cocobolo

Joined: Mon Apr 24, 2006 4:35 pm
Posts: 298
Location: United States
Good job Bob. We wouldnt want all that great wood damaged in an electrical fire.


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 19 posts ] 

All times are UTC - 5 hours


Who is online

Users browsing this forum: No registered users and 5 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
Powered by phpBB® Forum Software © phpBB Group
phpBB customization services by 2by2host.com